jdenison
Electrical
- Aug 27, 2009
- 4
What kind of problems should I expect with installing a vfd 100 ft from my motor that is 25hp 480v 33.7a w/ an Allen Bradley power flex 70 vfd. The conductor size I came up with is 3 - #6 thw-2 and a #10 grnd. Any suggestions on better condutors? I also came up w/ a 90a inverse time trip breaker ahead of the vfd any other opinions?