Hi all!
I'm about to start a re-design of some pumping and compressor stations supplied via VFDs. It will be good to know input power factor for large VFD. I suppose that there is a PFC circuit, but guess that it compensates only fundamental. So, with voltage distortion neglected, there will be: PF=cos phi1/sqrt(1+THDi^2). For example, 180kW input active power with cos phi1=1 and THDi=0,3 will give PF=0,958 and input apparent power of 180/0,958=188kVA.
Is my logic correct? All comments/links/experiences are welcome.
I'm about to start a re-design of some pumping and compressor stations supplied via VFDs. It will be good to know input power factor for large VFD. I suppose that there is a PFC circuit, but guess that it compensates only fundamental. So, with voltage distortion neglected, there will be: PF=cos phi1/sqrt(1+THDi^2). For example, 180kW input active power with cos phi1=1 and THDi=0,3 will give PF=0,958 and input apparent power of 180/0,958=188kVA.