edison123
- Oct 23, 2002
- 4,514
I tested a 415 V, 350 KW, 2 pole motor on no-load (open shaft).
With utility supply at 50 Hz, the motor winding temperature was 64 deg C with 130 A current.
With VFD supply at 50 Hz, the winding temperature went up to 97 deg C with the same 130 A current.
The drive is Yaskawa GA 700 model.
Where is the additional heat coming from? From the stator iron due to drive switching frequency?
Will using a sine filter on VFD output reduce the winding temperature?