Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

VFD for fan speed control

Status
Not open for further replies.

Lc85

Electrical
Joined
Apr 14, 2011
Messages
107
Location
GB
Hi,
We have a purge fan for a gas/gas heater.The current method to control the flow is to use an inlet box vane control. The client has proposed using a VFD instead. Would this mean that we no longer need the Inlet box vane and hence no actuator to operate it?

Thanks
 
Most probably. If you do not need the vane to shut off the fan duct when fan is at standstill.
If you need to shut the duct close when fan is off, you will still need the vane.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
And it is sometimes prudent to leave it in place in case you need to revert to it while the VFD is being byoassed for servicing.

"Will work for (the memory of) salami"
 
VFDs need servicing?? That's not what the salesman told me. 8-)
 
dpc
You need to RTFM - it's all there!

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
If the combustion air is from a different source the inlet vane may have to stay.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
dpc said:
VFDs need servicing?? That's not what the salesman told me. :looking around:
What? Believing salesmen again are we? I hear there's a 12 step program for that now called GFA; Gullible Fish Anonymous.

"Will work for (the memory of) salami"
 
Hey jraef: Haven't you heard? They removed the word "gullible" from the dictionary!

(My kids tried that one on me...)
 
Status