PLCSlick; You will likely see nothing of use with a clamp-on since all the issues are very fast and transient.
For a VFD to be 'simple' and energy efficient the drive outputs can only be fully ON or fully OFF. To get sinewave-like results the periods of time that the outputs are ON or OFF are varied simultaneously for all three phases in some fairly complex patterns. The ON/OFF periods are controlled by the carrier frequency which tend to be somewhere around 3 to 16kHz. The drive does math and figures out how many of these short ON/OFF periods are needed to result in the motor believing it is getting, say, 56Hz power.
For various reasons you can typically set the carrier frequency to different fixed values, often about 6 to 10 different frequencies. One of the common reasons you'd want to change it is for noise. At the lower frequencies motors usually make far more annoying audio 'whining' noise. However, at higher frequencies the effects of line charging, ringing, and drive output transistor heating all increase as do currents flowing about the system due to parasitic capacitance.
Part of the issue is just how fast the ON/OFF edges of the waveforms can change which has little to do with the carrier frequency because the ON/OFF is what it is for the output circuitry and drivers. However, the carrier frequency sets how often these transitions happen. How often they happen can drive various elements of the cable (inductance and capacitance) into resonances and into creating standing waves that can double the waveform voltages in some cases. That's what can trash the drive's output drivers and the motor's insulation.
The longer the cables the more capacitance. The more the capacitance the longer the actual drive output has to be ON for it to successfully charge up enough to get the power into the motor, also the more current that must pass thru the output components which heats them.
Turning the carrier freq down doesn't reduce the effects caused by the system and the ON/OFF edges but it certainly reduces the number of 'rings' and the number of times the drive has to try to charge and discharge the cable run and should have the drive output drivers running cooler. It may alter the tuned standing wave possibilities some also.
That's why we suggest moving the carrier freq down which is not the 'motor frequency'.
A bigger rated drive has less issues with it's output drivers expecting to drive larger currents thru bigger motors but instead driving more capacitive charging current. That's why that's on the table too.
A drive a month.. ugh. No chance you can move the drive to the conveyor? Use the existing cable to get the supply to the drive on the other end of the run?