You can do 10 ACH if you want to pay those energy costs. However, the 2006 IFC only requires that the mechanical ventilation system be designed to limit the volume of hydrogen in the room to a maximum 1% by volume -or - the exhaust system must be designed to exhaust air at a rate of 1 CFM/Sq.Ft. over the area of the room.
See 2006 International Fire Code, section 608.6.1.
Temperature control is also required for thermal runaway when dealing with valve regulated lead acid batteries (e.g., gel cells). However, some of the manufacturers have developed safety devices that de-energize the battery or battery string if it appraches a temperature to initiate thermal runaway. These devices are permitted to be used by IFC section 608.3.