Teto
Mechanical
- Feb 16, 2002
- 16
I have a question pertaining to VAV system operation/setup and would value your comments. First some background:I operate an 8 year old building with a VAV system. The AHU units have variable air volume controls on the fan (inlet vanes controlled by duct static pressure controller to 2" wc) and supplies air at 55 degrees to the building. The AHU units are strictly cooling units with economizers. In the building, the duct distribution system has terminal units on DDC with a reheat coil, pneumatic n.o. control valve at every terminal. I have no information on how the terminals are supposed to function as far as air flow is concerned. I have the prints with terminal box schedules showing 2 CFM designs. Example 2040/340 CFM. Is it safe to assume that the terminal will have a minimum air flow at 340 cfm? For heating, the control valve will start to open with the terminal damper staying at minimum? For cooling, the control valve will be in the closed position and the damper begin to open for and a maximum of 2040 CFM? Should the damper stop at the minimum position by mechanical means (it's a pneumatic actuator)? Should anything above the low CFM flow be considered cooling mode?. I would be happy to read any thoughts/comments on VAV terminal box setup and design.