reymen
Be careful if you are going to fit a VFD onto the Grundfos pump. The insulation class of the motors are typically not suitable for fitting a VFD directly onto the motor without fitting some type of sinusoidal filter between VFD and motor. Basic dv/dt filters are often not always suitable as the voltage stresses still impact the GF pump motor and I think therefore that GF will actually recommend a sinusoidal filter to ensure as close as possible a voltage sinewave.