Belden says so. But Belden has an agenda.
It depends a lot. There are at least four reasons why special cable may be good between VFD and motor. EMC is one, capacitve loading of inverter is another, ozone production and insulation deterioration a third and good, symmetrical PE a fourth.
You can run any motor/inverter on any cable. It will work, provided basic requirements are fulfilled. But you may get EMI problems and capacitive loading of the IGBT switches may be too high. Over the time, ozone production in the cable may, at least at higher voltages, lead to insulation being brittle and breaking down.
Motor reactors, du/dt filters and other filters reduce the problem. It is your decision. No definitive answer can be given without knowing the system and the environment.
If in doubt, use VFD cable in one installation and standard cable in another. In five years time, you will know what you need in your applications.
Gunnar Englund
--------------------------------------