The ONLY way a current limiting fuse can be used in this situation is if the VFD MANUFACTURER has tested and LISTED the VFD at a higher SCCR in a series listing. You cannot do this on your own in the field. This has been unsuccessfully argued may times in Code groups and forums, the bottom line is that the NEC does not allow for it. The closest is that IF a registered PE were to sign off on it, that might be acceptable. But in the 3 or 4 cases where this was tried near me, I have never come across a PE willing to risk his license for a little thing like this.
That said, most of the RESPONSIBLE VFD manufacturers have done this and will provide you with the necessary documentation showing you the EXACT fuse that the VFD has been listed with. By the way, there are often "Semiconductor" fuses, so be aware that if not provided as part of the VFD package, it can be challenging to find fuse holders for them that work in fused disconnect switches.
Under the old UL-508A rules for VFDs, this was more of a "dealer's choice" as to whether a VFD mfr wanted to provide a higher SCCR than the "courtesy" 10kA listing they can get without having to test. But in 2019, UL changed to "harmonize" with the IEC standards and came out with UL 61800-5-1 (the number matches the relevant IEC spec BTW) which REQUIRES that the VFD be tested and listed at a higher SCCR (usually 65kA or higher). So any drive still using the original UL-508A listing and ignoring this changed requirement is selling old product. If so, you might want to consider updating to something that will not be obsolete quite as soon. Even if it is older, it's still worth checking with the VFD mfr to see if they do have a series listing with specific fuses, many do.
I'll also throw in here that most of the time, under the new UL 61800-5-1 rules that are now more stringent, it has to be fuses, not circuit breakers. So you will now see a lot of VFD mfrs installing these fuses downstream of circuit breakers, regardless of the apparent redundancy. The fuses are generally over sized so that they don't clear unless it is a dead short circuit, leaving the day-to-day thermal over current protection to the breaker.
And YES, adding a Drive Isolation Transformer ahead of the VFD is a valid alternative solution, albeit expensive. I have done it several times. A Line Reactor however does not cut it.