Eng-Tips is the largest forum for Engineering Professionals on the Internet.

Members share and learn making Eng-Tips Forums the best source of engineering information on the Internet!

  • Congratulations dmapguru on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Valve fail safe action vs shutdown signal

Status
Not open for further replies.

helpyou

Automotive
Joined
Sep 26, 2011
Messages
79
Location
QA
Hi

Is fail safe action for a shutdown valve the same as shutdown signal.. for example, if we change power failure action of valve to fail in last positon.. does it mean when it receives signal from shutdown system, valve will not close , instead it stays at last position ? Or they can be configured to be different ..holds last position at power failure and closes at shutdown signal?

Your inputs please from experience ..thanks
 
To me, these are two different concepts.
The "shutdown" means to close down the stream and stop the flow. But, the "fail in last position" means to control the valve to stay at the current position while the system failed.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top