Hi Wilfred,
Let me rephrase my answer and interpretation over your question. But first allow me to synchronize common terms used, so we could have the same understanding:
a. Seat/side A is upstream side = side where source of pressure (in your case: nitrogen) is being applied
b. Seat/side B is downstream side = in closure test condition, this side should be pressure-less. An observation side for internal leakage. Normative, there should be nothing between obturator (ball/wedge/plug) and test fluid
c. Closure test = seat test = internal leakage test when valve in fully close position.
d. Test flange = a flange with nipple (usually threaded) hole. Function for nipple connection (hose/tubing)to 'safe location' medium.
e. Blind flange = a solid flange without hole (aside from bolting connection).
b. Test medium = any medium (liquid) which are defined by API 598 or have similar or smaller viscosity shall compared to water. Or gas e.g. nitrogen, air, helium
c. No visual leakage = for gas testing meaning no bubble visually seen (not even one bubble). for water meaning no water drop whatsoever.
d. How to apply test pressure? pressurized side A up to designated pressure, and after stabilized > close the regulator/valve from accumulator vessel and/or shut off the (booster) pump.
Now to your case:
You will apply 72.5 psi on side A presumably using direct a test flange connected to nitrogen bottle, valve in fully close position. However for some reason, on the other side you will apply Blind flange connected to side B flange (presumably with a proper gasket) > And will perform snoop method on this gasket circumferential?This is not allowed.
Soap should only be used for shell/body test, in addition with pressure drop noticed on the pressure gauge (located after pressure source). And also for leak detection for small tightened-able location e.g. nipple connection, flanges connection, etc. But not for seat leak.
Standard seat leakage is either bubble or water drop, and always quantitative. Hence it is impossible to do this with bubbly snoop/soap solution. Plus your method has one major flaw: any leakage will be 'stopped' by the gasket first before noticeable visually.
I only assume some situation restrict you from using a test flange (flange with a hole), what I usually did in the past in such circumstances is flip the valve, stem horizontal, side A facing below connected to nitrogen, side B facing up without flange. Apply pressure on side A, pour water on side B. Observe bubble on water pool B.
Still not doable, then drill your blind flange, install a straw, connect the straw to a glass of water. After usage, weld the hole again.
Regards,
MR
All valves will last for years, except the ones that were poorly manufactured; are still wrongly operated and or were wrongly selected