- Dec 26, 2001
- 85
I have an atmospheric storage (actually 20 in w.c.) tank with a flat bottom, 2:12 cone roof. It's not built to API 650 but looks a lot like one. I was wondering how high of vacuum rating it could take.
API 650 specifically says limit the tank to 1-inch w.c. external pressure.
FM Loss Prevention Bulletin No. 13.23 says 1 3/4-inch w.c. vacuum for roofs having at least 3/16-inch roofs.
Are there any other industry guidelines w/o perform a rigorous calculation???
API 650 specifically says limit the tank to 1-inch w.c. external pressure.
FM Loss Prevention Bulletin No. 13.23 says 1 3/4-inch w.c. vacuum for roofs having at least 3/16-inch roofs.
Are there any other industry guidelines w/o perform a rigorous calculation???