At the utility where I work, a new 27 kV gas insulted switch with vacuum interrupters is exhibiting inconsistent test results across A, B, and C phases. Here are the test details as completed by utility:
1) All phases passed 1-Minute 40 kV AC Hi-Pot Testing.
2) B Phase exhibited a decrease in IR during DC Step Voltage Test (2 to 10 kV DC for 1 minute duration over 5 minutes).
3) Compared to A and C Phases, B Phase exhibited inconsistent test results for both Polarization Index (10 kV DC) and Power Factor Tests (10 kV AC).
4) B Phase exhibited an increase in leakage current during 60 kV DC Test (15 minute).
Switch was sent back to vendor, who completed the following tests:
1) All phases passed 1-Minute 40 kV AC Hi-Pot Testing.
2) B Phase exhibited a higher leakage current during 60 kV DC Test (15 minute) compared to A and C phases. B Phase leakage current did not increase during test.
Vendor has advised that switch is ok and suitable for installation. Vendor advised that higher leakage current during 60 kV DC Test across B phase was likely the result of field emission phenomenon, whereby a microscopic sharp feature exists that is being observed during testing as increased leakage current. Vendor has advised that utility 10 kV tests (DC step voltage, polarization index, and power factor) do not provide any useful information on state of vacuum interrupters and that AC Hi-Pot test should be the ultimate means of testing integrity of vacuum interrupters.
Does vendor explanation sound reasonable?
1) All phases passed 1-Minute 40 kV AC Hi-Pot Testing.
2) B Phase exhibited a decrease in IR during DC Step Voltage Test (2 to 10 kV DC for 1 minute duration over 5 minutes).
3) Compared to A and C Phases, B Phase exhibited inconsistent test results for both Polarization Index (10 kV DC) and Power Factor Tests (10 kV AC).
4) B Phase exhibited an increase in leakage current during 60 kV DC Test (15 minute).
Switch was sent back to vendor, who completed the following tests:
1) All phases passed 1-Minute 40 kV AC Hi-Pot Testing.
2) B Phase exhibited a higher leakage current during 60 kV DC Test (15 minute) compared to A and C phases. B Phase leakage current did not increase during test.
Vendor has advised that switch is ok and suitable for installation. Vendor advised that higher leakage current during 60 kV DC Test across B phase was likely the result of field emission phenomenon, whereby a microscopic sharp feature exists that is being observed during testing as increased leakage current. Vendor has advised that utility 10 kV tests (DC step voltage, polarization index, and power factor) do not provide any useful information on state of vacuum interrupters and that AC Hi-Pot test should be the ultimate means of testing integrity of vacuum interrupters.
Does vendor explanation sound reasonable?