1. The switch breaking (making?) capacity is 200kA only if there is upstream protection device (breaker or fuse), otherwise is probably less than 10kA.
2. Problem may be not only the equipment in MDP, but also in subsequent switchboards if their breaking capacity is low (6kA or less). MDP is quite close to end box. In order to be sure, I would think about cascading the equipment instead changing the equipment in MDP. Cascading provides circuit breakers placed downstream of a limiting circuit breaker with an enhanced breaking capacity. The limiting circuit-breaker helps the circuit breaker placed downstream by limiting high short-circuit currents. Cascading makes it possible to use a circuit breaker with a breaking capacity lower than the short circuit current calculated at its installation point.
This means that I would install limiting circuit breaker instead of service switch. Important: cascading should be implemented only by using circuit breakers predefined tables made by their manufacturer. You should be able to find them in Schneider Electric, Siemens, ABB or GE site or in their catalogs.