Hello ALL,
This question is succession to my earlier question regarding reclosing. I appreciate the input.
On my 27 kV system, station bus has a fault 3 ph fault of 631 MVA, approx. 13000 A. The feede is a mix of O/H and U/G, run of 6000 m. Fault at customer main incoming primary 27 kV fused gear is 5300 A.
Customer primary gear feeds three transformers each, 5 MVA, 27/600V, %Z=6. A customer secondary 3 phase fault will reflect as 1340 A fault on primary.
Here is my question, as a utility protection engineer, am I supposed to pick a customer secondary 3 ph fault on 600 V on timed overcurren of my primary 27 kV station feeder breaker. Whom do I want this fault current to be seen. Secondary 600 V breaker clear or 27 kV primary fuse, what about my primary breaker ?
If yes, then do i want a secondary fault( 120/208V) on a 100 KVA pole top transformer unit to be seen by the station breaker the fault as well ?
I am sure I am missing something utility based protection application ? Thanks