I agree with Doug if the PCV is a self-contained backpressure regulator. Even then, it may be overridden with a solenoid valve on the (external) sensing line.
But if the PCV is a "CONTROL VALVE" it will follow any signal sent to it.
Current advanced state of the art control systems accomplish this easily. Just program in a function block to dump the valve open. Slightly more primitive systems may be more simply adapted by inserting a 3-way normally closed solenoid valve between the positioner and the valve actuator. With a fail-open (Air-to-close) control valve, chopping the power to the solenoid will isolate and vent the actuator, blowing the control valve to full open.
Blowdown can be pretty harsh service. High velocity, entrained particles are pretty tough on the valve trim and as cited in an earlier post, the valve may not shut off as tightly as before the blowdown. I remember once seeing a globe valve plug from a digester vent valve-which is not supposed to be as harsha service as blowdown, and it had suffered easily 50% material loss. Moral of this story: Use hardened trim, oversize the actiator for more seating load.
THis is an application where a ball valve can serve well. Use a full-port valve and get it open as quickly as possible. Then the high-velocity flow will not churn around inside the body doing damage, as it can with a globe-style valve with its S-shaped flow path.