I have situation where a contractor used ITW Trubolts to anchor some equipment onto an existing slab. The problem is that Trubolts are not rated to resist seismic loads only "Trubolt +" are. (Which he did not use) No the county wants pull testing done on the anchors.
I have done the calcs and I have ~= 1500# per bolt group and no net tension.
My question is: Can wedge anchors that are not approved (per their ESR report) for seismic loads be used if they are tested? If so, is there a code reference that can be followed? (IBC, or CBC) i.e. percentage of load that the bolt needs to be tested for.
Thanks in advance for any thoughts