jmaddox
Civil/Environmental
- Mar 20, 2013
- 8
I am planning on using full length #5 bars as hairpins to take the kickout force from the dead/collateral load in a premanufactured steel building. The idea is that the force will be transmitted to the slab and thus reduces the req'd size of my ftg. It is my belief that since I am using the slab to transmit load from the structure to the slab, the slab design is governed by ACI 318 (22.1.1.2). Because of this I am limited to the maximum reinforcement spacing (18") and minimum reinforcing ratios set by 7.12.2. (temp/shrinkage reinf.)
The reason that I am asking this is becasue the contractor wants to use #4's @ 24"oc in a 6" slab which violates both spacing and temp./shrinkage req's. Does anyone happen to know spacing/min ratio exceptions for this condition?
Thank you in advance for any thoughts on this issue.
The reason that I am asking this is becasue the contractor wants to use #4's @ 24"oc in a 6" slab which violates both spacing and temp./shrinkage req's. Does anyone happen to know spacing/min ratio exceptions for this condition?
Thank you in advance for any thoughts on this issue.