wzal, you should have no problems with a 3-6% oil carryover on performance. The greatest problem is in the evaporator where oil will tend to accumulate if not properly returned.
When there is oil in the evaporator, three factors determine whether or not it stays there:
·the viscosity or fluidity of the oil
·the velocity of the refrigerant gas
·the geometry of the piping.
Oil itself is quite fluid and has a relatively low viscosity at ordinary temperatures. At lower temperatures, the oil becomes more viscous. It becomes more difficult to pour or flow. At very low temperatures, it becomes solid
You might assume that oil is most difficult to move in the coldest part of the evaporator, but viscosity measurements show that this is not so. Refrigerant gas is more soluble in oil at low temperatures than at high temperatures at the same pressure—or, in other words, near saturation conditions. In many systems, the point of highest viscosity may be outside the evaporator. In this case, it would help to the suction-line temperature quickly go up. So, regarding oil return, the principal factor is the viscosity of the oil.