No, you are missing both of my points. 70 degree c ~ 160 deg F.
1. Hot, pressurized water for a hydrostatic test medium is dangerous. It does you no good, and is not needed. The unisulated pipes you need to handle and look at during the hydrostatic test are ALSO dangerous to climb around and look at and handle.
If there is a leak, the leaking/spraying/jetting hot water IS VERY dangerous!
2. You CANNOT heat the water to fill the boiler and feed piping and steam piping and isolation valves to start the test without some external (VERY expensive) temporary boiler. Once you have paid for that expensive hot water, the water cools off VERY quickly as the boiler pipes and walls and pipe and supports and valves heat up. So you don't have hot water anyway.
Why would you, your boss, your client, your plant want to pay for that?