Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Using a 3-phase generator for 1-phase load

Status
Not open for further replies.

KenRad

Mechanical
Joined
Sep 12, 2001
Messages
221
Location
US
I have a 3-phase 208 volt emergency generator that I want to use for single phase loads. Is there any problem with running the generator for prolonged periods while only using two of the three legs?

---KenRad
 
Why not install a 120/208 3 phase panel and balance your single phase load on all phases?
 
If you have access to both ends of all three windings you can connect them so that you get 120/240 single phase using all three windings. /\._ Each line is one winding, the dot is the neutral.
 

wareagle has the best suggestion—it permits full-capacity-genset loading. If no 120V loads are served, you could also jack that puppy's AVR up to 139V/coil and get 240V ø-ø times three.

For connecting “edison 3-wire” service to a 12-lead stator, see page 6+ of www.marathonelectric.com/generators/BROCHURE/GPN016.pdf   In all three cases reduce available power to two-thirds of nameplate.

DOUBLE-DELTA—SINGLE-PHASE CONNECTION  Most typical arrangement.

LOW ZIG-ZAG—SINGLE-PHASE CONNECTION  {Also termed “Le Blanc”} Less voltage balance with respect to neutral, and the fun of making two sets of 4+ wire pigtail wads.

HIGH-VOLTAGE—SERIES-DELTA CONNECTION   {Abandon/tape off “L1” external connection} Fine for 120/240V 3-wire if full neutral current is not needed {<50%.} Makes easier pigtail bolting/taping.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top