Please provide the users manual for the addressable heat and smoke detectors(Simplex and Notifier). I need to know the maintenance frequency and recommendations as per the manufacturer.
In general the manufacturer don´t mention frecuencys, just repfers or repeats the NFPA72 requirement (Inspection: 6 months, Testing 12 months) and clarifies that some applicactions may require more frecuent intervals.
Methods are mentioned in their I&M sheets (Magnet, Smoke chamber, Smoke spray can).