We typically use 12 x 12" oak timbers as cribbing for heavy equipment maintenance. Typical point load weights = 20,000 lbs . Would like to use aluminum tube instead of the oak due to fire code/ fire loading issues.
Assuming 6" x 4" tube, trying to determine thickness required to support 20,000 lbs point load . Assuming 6" flat on floor, I would treat each 4" vertical leg as a column. Assuming 1/2" wall thickness, compressive stress = 20000/(0.5 x 4") = 10000 psi << 0.6Fy = 0.6 (21000) = 12,600 for T6061 T6 aluminum ... OK ... Agree with this logic ??? Thanks..
Assuming 6" x 4" tube, trying to determine thickness required to support 20,000 lbs point load . Assuming 6" flat on floor, I would treat each 4" vertical leg as a column. Assuming 1/2" wall thickness, compressive stress = 20000/(0.5 x 4") = 10000 psi << 0.6Fy = 0.6 (21000) = 12,600 for T6061 T6 aluminum ... OK ... Agree with this logic ??? Thanks..