URGENT- Pressure drop across flexible bellows connection 1

Status
Not open for further replies.

d1010223

Mechanical
Joined
Mar 25, 2004
Messages
2
Location
AU
I've been asked to assess the reduction in cooling air flow due to the use of a flexible bellows joint between my ventilation duct and a locomotive traction motor...I want to set up a spread sheet to show reduction in area (due to pinching/closure due to missalignment) and resulting flow. I desperatly need a f or k factor or maybe a new equation to work out the pressure drop across the bellows and resulting reduction in airflow.


Any assistance would be greatly appreciated!

Adrian
 
SMACNA HVAC Systems Duct Design 1990 Figure 14-3 on page 14.9 charts duct friction loss correction factors for rough, medium rough, old, new and smooth ductwork at various sizes. Table 14-1 page 14.8 list flexible duct as rough category.
You should also account for elbows by inputing them as equivalent lengths.
 