I have a 6" roof slab, flat plate from the 70's. Due to a new slab opening and some increases in loading I have a column that does not meet punching shear requirements. There is no access to reinforce from below but I have complete access from above.
I have seen that Hilti has a post installed shear reinforcing system but they do not sell it in the US.
Has anyone done or seen a post installed upside down drop panel? We would roughen the existing slab. Then install some type of reinforcing, possibly drilled and epoxied diagonal bars... not sure of this detail yet. We would then pour a rectangular "drop" on top of the slab.
I have several concerns about doing this but my main one is developing rebar from the new upper panel into the existing slab.
Any thoughts on this?