I am sizing a suitable UPS with a given continuous load and an inrush value in both RMS and Peak Values.
The Transient Loading condition of a UPS is:
Transient KVA = ( Cont. Load KVA + Inrush KVA)*1.5
where: 1.5 = 150% UPS overload capability
Inrush kVA = Inrush kVA of the largest load
Cont. Load kVA = continuous kVA of the rest of the
load.
My question is, am I going to utilize the measured Inrush Peak or the Inrush RMS?