i have a situation where the ups room have transformer. the design using 2 AC (running and back up) to compensate the heat produced by the ups and an exhaust fan added to remove the heat produced by the transformer. my question will be can this design be effective for safe keeping of the equipment?
example:
ups-60KVA (as per catalog it produces 12283.2 btu/hr, so the room needs more than 1TR for cooling, i used wall type AC)
transformer-75KVA (from my calculation at least 400 cfm is need to remove the heat produce by transformer, the exhaust grilles is placed right above the transformer)
thanks