Gel-cells are typically not recommended for large UPS applications.
VRLA (valve-regulated lead acid) batteries are common. They also go by other common names such as sealed-cell and immobilized electrolyte (both terms also include gel-cell) and glass-mat absorbtion. VRLA is my preferred term. Anyway, they can be usually purchased with 5, 10, or 20 year warranties, usual life is 3 to 8 years. Advantages include low maintenance (almost no maintenance), little or no hydrogen off-gassing and little hydrogen monitoring requirements, ability to locate in cabinets, small footprints, may be located in general office/data center areas, etc. Also, the glass mat tends to absorb acid like a towel, so acid spills are of relatively low concern. Low initial cost but high lifecycle cost as compared to wet cell. Good for people who have better things to do than worry about their UPS and don't mind frequent battery changes.
Wet cell batteries are the other common battery storage. Off-gas hydrogen, detection usually required. Acid spill containment required. High maintenance. 20-year warranties are common, usual life is ~18 years. Low lifecycle cost. Bigger footprint, specialized rooms. Good for sophisticated users whose primary concern is UPS availability.
Rotary storage is making a comeback as a replacement for batteries, too. I have little experience with rotary systems, though. Most data center types stick to batteries, but I've heard that many manufacturing plants are installing rotary UPS systems.
Hope this helps.