MWTripper
Industrial
- Dec 13, 2010
- 2
Anyone ever try performing an upper sensor trim on a PIT by applying the same stable process pressure to a calibrated pressure meter as is applied to the PIT? Say I have nothing available to apply a URV of 5000 psi to a PIT, but my process pressure is steady at 4223 PSI. My transmitter output indicates an error (say its output is 4000 PSI)so I use 4223 PSI as indicated on the calibrated meter as my applied pressure for the upper sensor trim,to correct the error.