jechols
Structural
- Jan 21, 2004
- 109
I have a general question about uplift on a fully grouted masonry wall. I am looking at FEMA 361, Second Edition / August 2008, page 6-26 (166 of 374) Figure 6-4. Here is a dropbox link to that page:
This is a diagram showing continuous load path from roof to foundation. See position 3 in the diagram. It shows a steel roof beam bearing on an embed plate with hooked anchor bolt(s) into a masonry bond beam. It also shows vertical reinforcing extending into the bond beam.
Question: Would you consider this an interruption in the continuous load path? It seems to me that the vertical reinforcing would have to develop past the embed plate.
Secondary Question: If you agree that the vertical bar should develop past the embed plate, would you consider the point of beginning for the development length, the top of the hook of the hooked anchor bolt or the bottom of the embed plate?
My concern is that during the tornado the roof and single course bond would detach from the rest of the wall failing the storm shelter.
This is a diagram showing continuous load path from roof to foundation. See position 3 in the diagram. It shows a steel roof beam bearing on an embed plate with hooked anchor bolt(s) into a masonry bond beam. It also shows vertical reinforcing extending into the bond beam.
Question: Would you consider this an interruption in the continuous load path? It seems to me that the vertical reinforcing would have to develop past the embed plate.
Secondary Question: If you agree that the vertical bar should develop past the embed plate, would you consider the point of beginning for the development length, the top of the hook of the hooked anchor bolt or the bottom of the embed plate?
My concern is that during the tornado the roof and single course bond would detach from the rest of the wall failing the storm shelter.