the 2% rule is generally considered conservative. In fact, testing has shown that even 1% is adequate for uplift bracing.
Basically, find your maximum moment in the roof beam, calculate out the compression force in the compression flange, then take 2% of the force. Design a single angle for that compression (and tension) force over the span length of the angle.
If I have many beams side by side, like you say you have, I run a continuous angle across the bottoms of each. Then at the end (or also sometimes at some intermediate point), I X-brace the last bay, to bring the load up to the deck. If you do it this way, there is some debate as to whether the 2% at each beam is cumulative in the brace. Some say yes, some say no. Just to make sure I am convered, I add the forces up and design the angle for the total sum.
So lets say I have 8 W16 beams, spaced 5 feet apart, with a moment of 100 k-ft in each. So my compression flange force is 75 kip. 2% of that would be 1500 lb. So now if I only design a single brace from teh bottom chord up to the next adjacent top chord (L~6'), it would need to be L2x2x3/16. But if I run a continuous angle all the way across, with x-bracing at each end, the maximum force would be 8/2*1.5k, or 6 kip. Now the angle would need to be L3x3x1/4. So you can see, that it is not much of an increase in this case.
The last thing you need to worry about is how you resist the brace force at the end of the brace. Typically you would bring it back up to the deck diaphragm. So now you have to ensure your deck can take the point load, or figure out how to distribute it over a large enough area. And you should consider the normal deck stresses (uplift, diaphragm shear) due to the wind event at the same time as your uplift brace load. This can result in additional deck fastening in the area of the brace.