So, your turbine has a curve of efficiency vs. load, as does your boiler, but then too all the components in the water cycle do too, feedwater heaters, condensers, etc. To make a reasonable curve, one would have to consider the effects of partial load on each of them. Your turbine may have a set of heat balances for various load points that would define the turbine efficiency as a combination of the turbine and FWH's, BFP's, etc., but it doubtfully has any accomodation for the boiler's part load efficiencies.
If you have good technical performance data on all your major pieces of equipment, you should be able to develop it in fairly short order. I can remember having to do just that some years ago.
Remember too that the plant's heat rate incorporates the aux loads as well, and some of those do not diminish as load falls off. The circ water pumps, for example, pump just as much water at 50% load as they do at 100% load. So does a lot of other equiment in the plant.
rmw