It seems the dispute is over whether the bottom chord is required by code to be designed for 10 psf storage in addition to 20 psf live load.
For the sake of this discussion, I read the commentary. 1607.11.2 Minimum Roof Live Loads
There it states: ....the minimum roof live loads typically occur during roof maintenance, construction or repair.
Then looking at Table 1607.1 If the attic space is uninhabitable without storage, use 10 psf load. So that applies to the bottom chord for who knows what purpose? But that chord or ceiling joist must be designed to carry that minimum load.
Now move from the attic to the whole truss. Now the loads prescribed have a purpose - maintenance, construction, or repair.
Unless otherwise specifically stated for that purpose, the ceiling space for the truss is not designed for storage. And if it is specifically to be designed for storage, then it is to be designed for a minimum of 20 psf. And if that were how it is to be designed, then it would include being in addition to the roof live load of 20 psf for the purpose of maintenance, construction or repair, if it is part of a truss since this is an ongoing design load criteria which must be considered. The roof will need to be repaired even while there's stuff up there.
So what's the minimum standard? I think we have one without penalizing anyone unnecessarily. If someone wants a storage space, declare it, and pay the extra cost for it understanding that the code does not require it to be provided as a minimum roof function. If the space is designed for storage, then do so safely and without need to worry about crashing through the ceiling. If it's not designed that way, be careful, you take a risk.