I am reviewing calcualtions for a braced frame connection. The contractor took the liberty of fabricating and erecting the steel, before we even recieved design calcs or shops drawings. The connection is what is typically shown in AISC heavy diagonal brace connections where a beam, column, and diagonal brace meet at a single work point. The connection is very similar to what is shown in AISC 2nd ed. LRFD Vol 2, Fig. 11-7. The gusset is bolted to the column and welded to the beam. The beam is bolted to the column.
My issue with the calculations are that the gusset to beam connection is detailed in such a way that alpha and alpha-bar are not equal (ideal centroid for no moment on connection and actual centriod with respect to column flange). This in turn induces a moment on the gusset to beam interface (which is indicated on the calcs i am reviewing). My thinking in looking at the free body of the beam is that this also induces an end moment in the beam as well that we did not design for. The connection designer is stating that the method takes into account this eccentricty and is not affecting the beam. The only thing that I can think of is, that perhaps he is assuming that this moment at the beam/gusset interface is resisted by a couple created at the beam/column connection and gusset/column connection, but it seems to me that the load path still needs to go through the beam first. And the horizontal forces on the beam/column and gusset/column connection do not seem to indicate this.
I would appreciate any comments that anyone may have regarding that if there is a moment induced at the beam/gusset interace, then this needs to be resisted by a moment in the beam. Thanks in advance.