Good people,
Does anybody know of a practical way how to bring 2500 Amps @ 4160 V underground connection to MV Switchgear ?!!?!
My problem is that after applying the ampacitis from NEC Table 310.77 Detail 3, the net result is about 7 circuits of 750 KCM.
And here starts the problem:
I can opt for 9 x 500, which would give me an ampacity of 2950 according to the table, but detail 3 only considers 6 conduits in a ductbank.
I can opt for 9 x 750 which will give me ampacity of 3555 (MV-105), according to the table for 6 conduits.
Here comes the second problem:
a/If I go with 500 KCM option - my ampacity is unknown, but for sure is less than the breaker rating of 3000 Amp.
b/If I go with 750 KCM option - my ampacity is still unknown, it will be less than the breaker rating, and the conduit should be 5".
Having said 5" conduit - here comes the third problem:
The bending radius of a 5" conduit is minimum 60". NEC allows me to go maximum 36" deep counted from the top of the first conduit layer of the ductbank.
On the up side - my SWGR rep says that they very rarely see so many conduits coming into a 3000 Amp SWGR. So apparently either I am missing something or everybody else knows something that I do not know.
Some people suggested using buss duct. However, I do not see a way of putting buss duct without building a tunel, so that the electricians can walk.
PLEASE HELP. I FEEL LIKE I AM CHASING MY TAIL HERE.
Thanks
Ted
Does anybody know of a practical way how to bring 2500 Amps @ 4160 V underground connection to MV Switchgear ?!!?!
My problem is that after applying the ampacitis from NEC Table 310.77 Detail 3, the net result is about 7 circuits of 750 KCM.
And here starts the problem:
I can opt for 9 x 500, which would give me an ampacity of 2950 according to the table, but detail 3 only considers 6 conduits in a ductbank.
I can opt for 9 x 750 which will give me ampacity of 3555 (MV-105), according to the table for 6 conduits.
Here comes the second problem:
a/If I go with 500 KCM option - my ampacity is unknown, but for sure is less than the breaker rating of 3000 Amp.
b/If I go with 750 KCM option - my ampacity is still unknown, it will be less than the breaker rating, and the conduit should be 5".
Having said 5" conduit - here comes the third problem:
The bending radius of a 5" conduit is minimum 60". NEC allows me to go maximum 36" deep counted from the top of the first conduit layer of the ductbank.
On the up side - my SWGR rep says that they very rarely see so many conduits coming into a 3000 Amp SWGR. So apparently either I am missing something or everybody else knows something that I do not know.
Some people suggested using buss duct. However, I do not see a way of putting buss duct without building a tunel, so that the electricians can walk.
PLEASE HELP. I FEEL LIKE I AM CHASING MY TAIL HERE.
Thanks
Ted