rockman7892
I was at a facility the other day that was being set for startup when a discussion arose on how ground fault detection would work. I wasn't familiar with the project and was only a visitor so I stood in the background just listening. Of course after listening and hearing the discussion I have a few questions of my own.
I have attached a brief sketch of a One-Line for the facility in question. As you can see they will have several generators at 4.16kV (only show 2 on sketch) that will be operating in parallel with the utility to serve other loads at the facility and possibly feed back to the utility. The generators are impedance grounded at 4.16kV and feed through a step-up transformer to a 13.2kV bus to feed the other loads in the facility and the utility. The LV or generator side of the transformer is Delta and the HV or 13.2 KV side of the transformer is a reactance grounded wye.
The question first arose when it was noticed that there was no CT on the reactor or neutral bushing of the Generator Transformer primary. The question then was without a neutral CT how will ground fault be detected for faults on downstream feeder circuits on the 13.2kV bus. I did not show all of the CT's in the sketch but both 13.2kV and 4.16kV buses have a differential bus scheme protecting the bus. Saying this most people in the conversation seemed to think that becasue there was this bus differential protection faults at the downstream feeders (as shown on sketch) would be detected by the bus differential relay. I should also mention that there is a transformer differential relay scheme used on the Generator transformer.
I do not believe this to be correct for I dont think a ground fault at the downstream feeders will be detected by either the bus or transformer differential schemes because they are outside the differential zones so the differential protection current in will equal current out..
My thought was that you should be able to detect ground fault with the zero sequence CT and settings used on the feeder breakers. Would this be an adequate way of detecting ground fault?
Now I should mention that the neutral reactance on the generator transformer limits GF current to 200A.
Also if both the Generators and the utility are operating in parallel and since the utility is solidly grounded for a fault on the downstream feeders wont some of the fault current come from the utility while some came from the generator transforemr?
I'm interested to hear others input and hopefully learn from them.
Thanks for the help.