Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Under Current Protection Application

Status
Not open for further replies.

SMB1

Electrical
Jan 15, 2003
85
Hi,

can any body explain the application of under current protection in capacitor bank feeder?
 
Replies continue below

Recommended for you

Possibly to detect open capacitors.?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
thanx all,

Bill & Slavag
unbalance protection will detect open capacitor.

is it the same application?

 
Hi SMB1.
Is not same application.
Undrcurrent protection is detected disconnection of capacitor bank and prevent a reconnection with some timer.
Is operated only if ALL 3-ph currents are below some set point ( of course not before connection of CapBanks).

Unbalce protection base on the meas in the CT installed betwen two starpoints of banks.

Best Regards.
Slava
 
I'm afraid I've never heard of anyone applying undercurrent protection to a capacitor bank.

I would expect that the capacitor can would fail shorted and an overcurrent condition would be detected.

Can you explain where this is used and how the undercurrent condition ignores normal load current?
 
The undercurrent would be looking for something sufficiently less than normal load current. Fused cans will fail to an open condition and current will go down.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor