rharting
Structural
- Dec 17, 2007
- 41
I have an addition to an existing building. The existing building is approximately 150' long with a relatively flat roof. The new building is a hip roof with 25' eave to ridge distance and a slope of 3 on 12.
I believe i should be treating this like a hip roof (with an unbalanced load) with the lu equal to the full build up of snow = 152'+25' (similar to a high roof). Using a 35 psf snow load, my hd would be approximately 4.45' and thus making my unbalanced load of ~42 psf with a width of almost 24'(using figure 7-9). If i consider lu to be only 25' (7.6.1 states that the lu is equal to the eave to ridge distance) this decreases my unbalanced load to 16.1 psf with a width of 9'.
I believe the latter neglects the full buildup of the snow which was not the intent. I also considered using the full buildup on the side opposite the exsiting building and the 25 for the side adjacent (considering there is no 'build-up'), but this would then neglect buildup on the windward side. So while it seems ultra-conservative, i think i need to design both sides for the full buildup of snow which takes my snow load from a balanced 35 psf to an unbalanced 77 psf.
Any agreements or thoughts?
I believe i should be treating this like a hip roof (with an unbalanced load) with the lu equal to the full build up of snow = 152'+25' (similar to a high roof). Using a 35 psf snow load, my hd would be approximately 4.45' and thus making my unbalanced load of ~42 psf with a width of almost 24'(using figure 7-9). If i consider lu to be only 25' (7.6.1 states that the lu is equal to the eave to ridge distance) this decreases my unbalanced load to 16.1 psf with a width of 9'.
I believe the latter neglects the full buildup of the snow which was not the intent. I also considered using the full buildup on the side opposite the exsiting building and the 25 for the side adjacent (considering there is no 'build-up'), but this would then neglect buildup on the windward side. So while it seems ultra-conservative, i think i need to design both sides for the full buildup of snow which takes my snow load from a balanced 35 psf to an unbalanced 77 psf.
Any agreements or thoughts?