cbark
Electrical
- Aug 5, 2011
- 11
We had a fault on a feeder off the the secondary of a Delta-Wye transformer that caused the primary overcurrent relays to operate. The relays that operated on the primary are electromechanical relays, so they don't provide any indication as to the fault current values. The secondary relays are SEL and had event captures so we know what the secondary currents were during the fault. I'm trying to determine what the primary currents were based on the secondary fault currents. Below is the system information and fault data.
Transformer Information:
Primary: 138 kV - Delta
Secondary: 13.8 kV - Wye Resistance Grounded (400 A)
Rating: 30 MVA
Z% = 8.2%
Fault Currents on the Secondary:
Ia = 11392 @ 180.8 degrees
Ib = 10411 @ 6.4 degrees
Ic = 1438.6 @ 316.2 degrees
How do I determine what the primary currents are for each phase?
Transformer Information:
Primary: 138 kV - Delta
Secondary: 13.8 kV - Wye Resistance Grounded (400 A)
Rating: 30 MVA
Z% = 8.2%
Fault Currents on the Secondary:
Ia = 11392 @ 180.8 degrees
Ib = 10411 @ 6.4 degrees
Ic = 1438.6 @ 316.2 degrees
How do I determine what the primary currents are for each phase?