During a short circuit test on a brand new 100 MW hydro generator, at each excitation level, the phase currents were found to be different (7098 / 7042 / 7056 A; 6790 / 6734 / 6748 A down to 602 / 560 / 574 A). The ammeters used for this test are calibrated and checked for the same reading by connecting them in series and passing a known current. ( I even switched around the ammeters and still found the above pattern of the differing phase currents). Also, the CT’s were brand new from reputed manufacturer and had been calibrated prior to SC test with primary injection. What could be the reason for this consistent different phase currents under short circuit ? Does the fact that the stator winding is fractional slot winding has anything do with it and if so, how ? Has anybody else seen the same phenomenon ?