R(280,120,87,97,188)
S(300,275,95,85,185)
T(320,264,99,180,85)
The current in the cables is different and the CT is working ok.
A few questions :
1) Is a similar unbalance seen in the S&T Phase
yes
2) Is there a neutral on the system
No 3 winding XFMR (19/6.6KV 32MVA)and 2 sec winding going to 2 SWGR incomers each incomers have 15 cables (5 per phase each is 300mm`2
3) What cables are installed
1x300mm`2 6.6KV cu with cu screen XLPE /PVC
4) What is the expected load?
16MVA
5) Have you a CT on each cable? or are the figures from a clamp on meter
we have one CT for each phase and 3 part of bus bar from CT and 5 cables connecting to 3 part of BB
6) How are the cables installed,
a)Cable Tray
b)spacing between cables(don`t know)
c)flat
d)Are there other cables installed along the same run
yes (30cables MV 15 per each incomer)
e)Are the cables earthed at both ends or just one?
just once
f) What is the cable Length
170m
If you are using a CT installed on each cable
no
possible issues may be
1) Current flowing in the screen/armour may be
2) currents in the screen being measured onone CT and not on others
3) Current imbalance due to cable arranbement i suggest this but i wonder of this big difference
4) Poor teerminations on some cables we repear termination with torque 85NM for bolt12