I'm going to have to call you on that one NJ. Or at least ask you for citation. Going over the Hosemonster website site for instance, I find no reference to anything other than an FM listing for flow rate accuracy. Whatever that might mean. I see nothing under 25, ch 4 - 2011 ed, and specifically 4.5. Pitot tubes are not listed. I buy and maintain fairly expensive gauges for testing purposes but they are not listed, nor does a quick google lead me to any such device (for testing that is... Ashcroft for example does have gauges listed for fire service). I have my gauges calibrated annually and keep certificates filed, and note the particular test kit number and serial numbers of the kits used on inspection reports, but I do that out of prudence: if I'm asked to justify how I attained certain test results, being able to show I have accurate equipment is a good start. Actually I'm somewhat puzzled by the dearth of information or requirements regarding this, especially in 25. The FPH (20th ed) is silent on the matter also, and actually this is where I had hoped to find a lot more information related to testing practices and the equipment used.
Regards
Dave