We have been performing offline IR/DDF and PD tests phase to earth and phase to phase on our 11kV switchgear for probably 30 years now, and have found many problems with both DDF and PD.
We have trialled the PDM (multichannel TEV PD monitor with a number of input channels and a few antenna channels to remove outside noise) and Micro TEV (handheld unit) instruments, and had mixed success with finding PD problems. Although there is no calibration possible, we tried to get a rough comparison between the dB readings, and an actual discharge. In most cases we found that there needed to be a discharge of around the 1000pC mark before the micro Tev got to an orange state, and that the dB levels in the PDM showed above the recommended values. Discharges at this level are of grave concern, and ones that would not go back in service without entry restrictions on the substation.
Our main concern is that whilst PD detection is a condition monitoring tool, we have found more issues with DDF rising over time than discharges in our gear, so we would be taking the group out of service to do DDF tests anyhow. Thermal runaway on the insulation in this type of switchgear, at the age of some of our gear can be a problem.
I cannot give any comment on the Mini TEV, however I believe that one of the drawbacks of the Micro TEV (just having a red, orange or green light for condition indication) has been improved to have the actual dB reading on screen. We hope to trial this unit soon, which we might use more as a safety indication for staff entering substations.
My belief is that these units (TEV monitors) would be a reasonable ranking tool, if you have limited test capability or staff, to plan which are the top (worst) say 10% of switchgear (from a PD point of view) you want to target with offline testing.