Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

UL Design Number and Detail

Status
Not open for further replies.

madvb

Mechanical
Joined
Dec 16, 2002
Messages
41
Location
US
Hi all,

I'm designing a project that requires fire sprinklers in the building. Since we don't have a specialist in fire sprinkler, I'm just going to do a performance specifications for the fire sprinkler system and have the contractor design/build the fire sprinkler system. The plans and performance specifications was sent to the State Fire Marshall (SFM), and it came back with a comment from SFM saying to provide a UL Design Number and Detail. I don't understand what this comment is asking. Where would I find this information when all I'm doing is the performance specifications and have the contractor design/build? Should that be my response to the comment?

Any help is greatly appreciated. Thanks.
 
You probably have a rated corridor. The corridor is probably required to be 2 hour rated but with fire sprinklers the rating can be reduced to 1 hour. The SFM wants clarification that the wall will be constructed to a standard such as UL U419 which requires a gypsum board on each side for a 1 hour and double gypsum board on both sides for a 2 hour wall. The UL rating may also have how many fasteners are required. Make sure dampers are in place where needed.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top