type of fire loops
zicoo000
15
hi every body
can explain the the type of main loop?
because when i design closed loop (rectangle loop ) and the branches is feed from 2 point.
some one say to me it's wrong, he say i must cut this branches (like FIGURE A.3.4.7 Looped System. nfpa 2010)
please advice me with source NFPA
regards
NFPA 2010 is a standard for Fixed Aerosol Fire-Extinguishing Systems, so is that the standard that you are referencing? also, since it appears that English is not your primary language, you should give us a full sketch of the system for which you are seeking the help of responders.
The looped system does NOT have to be like in that example. All a loop means in that the crossmains are connected to create a closed "loop" and are not dead ended. It doesn't matter if the branch lines are end fed or center fed. That picture is just a diagram of a simple example.
I had assumed the original question was from NFPA 13, 2010 edition.
Travis Mack
MFP Design, LLC
TravisMack, my deceased thermo. teacher once told me back in the late '60's that assume makes an A$%^& out you and me and I never forgot that particular lesson.