tyco attic head
cdafd
Specifier/Regulator
Aug 18, 2005
2,939
Has anyone seen a tyco attic head used in an arched ceiling/ attic???
Attics yes, ceilings no.
From my understanding of the Tyco Attic Sprinklers they are listed for attic spaces (combustible concealed) only.
For these spaces they are a great technology that reduces the amount of piping required by a large percentage. A single line at the peak can reduce several rows of lines and all the obstructions and headaches that follow.
I believe these are only listed for slopes of 4:12 up to 12:12. All of the diagrams indicate a peaked roof and not an arched roof.
As stated above, my understanding is that they are only listed for concealed combustible spaces and not in non-concealed installations.
Travis Mack
MFP Design, LLC
Sorry was trying to say the attic roof line is arched
But a follow up question, If the roof line is flat can you use the tyco attic head????
I think I missed your point entirely. No, I have not seen them used in arched roofs. Per the listing it seems the attic sprinklers are listed for flat, sloping roofs.
sorry started off with one question and added
1. if the roof line is "arched" can the tyco attic head be used, or is this outside the listing??
2. if the roof line is flat can the tyco attic head be use, or is this outside the listing??
check page "7" say for the "BB3" it appears for it and any of the heads there is a minimum and maximum slop that is "REQUIRED"
For the BB heads, you must have a minimum of 4:12 pitch. I believe that they may have expanded one of the heads to 3:12. The AP heads can have a minimum pitch of 3:12.
Remember, if you have a flat roof and <36" of clearance, you need the Tyco CC1/CC2 sprinklers.
Travis Mack
MFP Design, LLC
travis
thank you for the confirmation, and the reminder
somewhat luckily, these are kind of big void combustible areas