- Feb 23, 2002
- 47
Hi,
i am trying to replace unknown model txv of 75ton trane chiller(one circuit),i fixed a 55ton (ove55-cp100- nominal)txv which is running in 125ton york chiller (two circuits),but parameters were:
suction pressure : 45 psi (very low)
leaving and return water temp: 40 c
condensing pressure : 220 psi
no buubles in sight glass
compressor 33% loaded
do you think the new txv is small,why it is running with that york chiller.
i also replaced liquid line solenoid valve befor that txv.
i am in saudi arabia with 47c ambient temp.
thanks.