Good afternoon Eldorado,
For 2-way PT (and PT in general) it's important to consider restraining conditions, tendon layout, stressing locations.
- Tendons will "pull" the structure toward locations of higher restraint so imbalance in lateral stiffness and eccentric LFRS placement should be avoided. For example shear walls located at one end of the floor plate will be an anchor and the remainder of the structure will shrink towards it.
- For multi-story construction floor plates will tend to shrink in overall dimension, cumulatively, if columns are positioned plumb around the perimeter. Specifying a slight outward tilt may be necessary.
- Cracking can occur at retaining conditions such at floor along shear walls. For highly stressed slabs it may be necessary to place delay strips in the slab or wall.
- Two way slabs normally have a primary stressing direction where the tendons are banded in the column strips and a secondary direction where the tendons are placed at a uniform spacing. This helps reduce the number of conflicts for the tendon drape.
- Placing tendons at openings is a bit of an art. Sometimes you stop them at each side of the opening (requiring additional reinforcing around the opening) and other times sweep the tendons around the opening, typically if they are smaller.
-Consider the locations for stressing the tendons. One end can be a dead end anchor with no access and the other a live end where you'll be placing the jack and having a place to stand to do the work. You can possibly pull a tendon up to about 200 feet from one end but I wouldn't recommend it if you can have access both ends and pull both ends. Slab edges will need to be plugged and patched at the live ends.
-Sometimes you can be blocked from getting to a live end at the perimeter of a structure. Blockouts/pockets in the interior of the slab can be placed to allow stressing.
This I'm sure is only a beginning to the list. If you have any PT contractors in your neighborhood now is a good time to introduce yourself.
regards,
Michel