Hi, Please questions below:
1. I am responsible for the performance, maintanace and condition monitoring of six 600 to 700MW generators.I have since observed that at higher MW and MVar the stator core temps are increasing proportionally but some other sections on the core, particularly the end of core plates, temperatures at times reaches alarm point and this i have seen on all units. I have since tried to inform the OEM of this problem thinking that it might be design defect or something. I have also checked the RTD on the back of core and no signs of overheating. Can stator core grounding have an effect on the temps? The machines operate within the capability limts.
2. I am trying to compile the effect on stator and rotor due two shifting operation. Am specifically worried about the stator since so much is been given to the rotor so far.
3. Does the H2 pressure as well purity have any effect on the levels of partial diacharges and how accurate is the PD in assesing the insulation.
4. Can any one suggest the operator's response during Generator Condition Monitor alarm, one cannot just trip the unit due to the alrm from the GCM-X.
1. I am responsible for the performance, maintanace and condition monitoring of six 600 to 700MW generators.I have since observed that at higher MW and MVar the stator core temps are increasing proportionally but some other sections on the core, particularly the end of core plates, temperatures at times reaches alarm point and this i have seen on all units. I have since tried to inform the OEM of this problem thinking that it might be design defect or something. I have also checked the RTD on the back of core and no signs of overheating. Can stator core grounding have an effect on the temps? The machines operate within the capability limts.
2. I am trying to compile the effect on stator and rotor due two shifting operation. Am specifically worried about the stator since so much is been given to the rotor so far.
3. Does the H2 pressure as well purity have any effect on the levels of partial diacharges and how accurate is the PD in assesing the insulation.
4. Can any one suggest the operator's response during Generator Condition Monitor alarm, one cannot just trip the unit due to the alrm from the GCM-X.